[Need Help] VijeoCitect problem when set to TCP/IP

hadihidayat

Member
Join Date
Mar 2010
Location
Batam
Posts
11
I build the project in Vijeo Citect 7.10. That was fine when run in "No Networking" mode. But when I set to "TCP/IP", the problem occured, I can not change the value of "variable tag" (the button I created to toggle "symbol set" tag was no effect). also, the display in other PC (using web browser) was incorrect (i.e. symbol set filled by grid).
Any suggestion?
 
This problem occurs because the server address has not been set.

with Vijeo Citect,
1. from Citect Editor, menu Servers, Network Adresses,
a. create address name,
b. set IP = IP PC server.
2. from menu Servers, IO server, set Network Address to the IP of Network Address on step 1.b.
3. do the same for Alarm server, Report server dan Trend server.
4. Pack
5. COmpile + Web deploy
6. Run

with Browser,
7. do web deployment for this projek.


Hope this help you.
 

Similar Topics

I was wondering if anyone could help i am trying to use a SLC 500 with a 5/05 processor to set up an incremental encoder to a HSCE2 card? The card...
Replies
1
Views
91
I have an old Sentry Palletizer (S/O Number 3007 / Serial Number 1172) that has lost its program as the backup battery died years ago. I can...
Replies
0
Views
148
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
99
I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
402
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
11
Views
242
Back
Top Bottom