Hello,
I'm an intern at this power plant and I'm new to PLC programming. I'm hoping to get some help from the professionals in this forum.
I ran into a problem while working on adding a PID loop that controls a heat exchanger outlet temperature for an air dryer system.
The controller include:
- Micrologix 1200
- 1762-IF4 module
- 1762-IF2OF2 module
The problem:
- I added an PID function on a separate program file with a SCP function to scale the data for PID loop. Somehow, the SCP function keeps giving ZERO output.
+ SCP setup
input: I:1.3, input min: 6241, input max: 31206
scaled min:0, scaled max: 16383, output: N7:41
- The temperature input (I:1.3) comes from IF4 card which was not "Scaled for PID" by the original programmer. T3 is in correct range.
- The PID controls an output of IF2OF2 card which connected to a proportional valve.
- There are other SCP functions used in a different program file and they are working fine, including (I:1.3) input but different scaling unit.
- I tried to use SCL but it gave ZERO output as well.
Please help!
Thank you!
- Micrologix 1200
- 1762-IF4 module
The problem:
+ SCP setup
Please help!
Thank you!