Need Help with Omron CP1H
Manthan
Jul 2022
Milton
36
I have a question about SET instruction in Cx-programmer. When condition goes true it is supposed to give value 1. But, my controller is giving 0. As you can see in the attached picture. All I want to know is how? And why? Is there something I am missing?
Rung 7
SET > H77.00 > should give 1 but giving 0.
Rung 8
H77.00 NO contact should give 1 as soon as SET gives 1.
Not familure with CX or Omron but one of two things:
Either it is being reset elsewhere i.e. RST H77.00 (Do a search for that contact) or if this bit is part of either some communication card or special card it could be being reset within the special card by it's own software, I know this happens in some other PLC's.
So, that H77.00 bit is used to turn on T39. T39/DN resets H77.00.
Reset bit turns on T16. T16/DN bit SET H77.00
It is being used to turn on and off solenoid signal until MAG_XFWR_SER2 detects MAG.
T39 OFF resets H77.0? Is this what's happening?
Both of these set and reset H77.0 from what I am reading.
Sorry, not T39. T25 it is. See attached picture.
So, this how program works.
T16 would turn on at the start of cycle. And if there is no MAG on conveyor, it would SET H77.00. As soon as SET H77.00 gives 1, it turns on T25. T25/DN goes to RSET H77.00
RSET H77.00 turns on again T16 and if still no MAG at sensor, repeat the cycle until sensor detects it.
Sounds to me it's doing what it's supposed to if there's no MAG at sensor. The PLC sets H77.0 and immediately resets H77.0 because there's still no MAG at sensor. The scan time of the PLC is so fast that you never see H77.0 turning on with the SET instruction.
You can right click on H77.0 and select Differential Monitor (and rising) to see if H77.0 actually changes state.
By looking at it, count stays 0 on rising edge all the time.
Something else must be keep the value at zero then.
Can you do a 'Find' in PLC for this address (H77.0) and see where it's used?
I have gotten caught before because there's a BSET (or MOV) instruction somewhere else in the code to always made a word to zero.
If you can, send a screenshot of the cross reference report for H77.0
Maybe there's something that we are missing if we look there. This is quite a mystery.
Did it work before ?, is the program working if so then it will not be a program error, it must be something else, if the logic for that bit is working then it could be that it is too fast for monitoring.
Yeah, it's really weird. I don't see what else it can be in the PLC code.
Not sure if you have a HMI also that can be setting this bit to 0 indefinitely. This has happened to me before. There's some mode on the HMI that someone programmed to reset a bit indefinitely.
@parky
Yes, Program was working fine. Line was down from a long time. We have been asked to get it running for production. So, fine tuning was needed here and there.
If it was related to something else, solenoid or connection, I would have found that out. When I do force On/OFF, cylinder extracts and retracts. I don’t see o/p LED coming up, even for a sec. But, with force on/off, it does.
Hi, I don't have any formal education background with PLC. I am learning PLC by myself. I have CJ2M CPU34 unit and CJ1W-DA021 unit. I would...
1,258
Hey all, I am working on this new project where i am devloping hmi in cx desiner , i have one question if i want a screen which only shows on...
1,742
hello guys I'm having problem in pid in Omron cp1l plc I have program . I'm getting alarm when I execute pid
2,831
Good day all, Newbie here so I'm practising my posting skills. I have a problem with one of the Omron C200HG PLC''s in our plant. This particular...
1,486
Dear all PLC's master, I'm trying to connect CPM1A to rotary encoder (Omron E6B2) using PRV with this code (0 0 DM100), but i can't read the...
6,200