No Comms w/ 1785-L11B
rwensley
May 2008
Wisconsin Dells, WI
I am trying to communicate with this PLC from laptop/RSLogix Com1 to CH0 on the processor and can not establish comms. I have verified dip switch settings and cable connections.
Any help is welcomed.
Ron
See procedure below. Do you have a real serial port or a USB to serial adapter. Not all USB to serial adapters work.
Still No Comms
I cut apart the cable and made the connections as per the pdf. and reverified. Still no comms using the Auto-Configure button.
Any other help?
Thanks,
Ron
Have you checked the switch settings for the serial port?
Also, there is the possibility that the port is set for user mode. If so, then it is possible to send ASCII control characters to switch its mode back to system (DF1) which is what you want to use with RSLinx.
Do you have an offline copy of the program?
Do you have the means to connect to the PLC5 via the DH+ channel?
That's all I can think of right now.
Tell us a little more about this PLC. Is it a working PLC? ( controlling something or are you just trying to learn). Was there, is there something connected to the serial port? If its not controlling anything then you can reset it to its default condition by removing the battery. Don't do this if its controlling something.
Double check your cable ( you need a null modem cable)
The PLC 5/11
Was removed from an old turbine control system that has been upgraded. I have now idea what the program is on the plc. I do know that it used the serial (CH0) port to interface with a westinghouse P-2000 control computer.
I am trying to set this up as a trainer so removing the battery and losing the program is not a problem. I will also purchase a new null cable and see if that resolves the issue. I'll let you know.
Thanks for the ideas,
Ron
The PLC 5/11 also uses DH+ , do you have it available to you.
If you can get online with DH+ you may be able to see if the RS232 port is configured for a different comms set up
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
127
Hello, can someone share/explain How to check comms between PC and PLC via TeamViewer? TIA
413
Has anyone setup communications with Red Lion 3.0 MODBUS to Baker Hughes Centrilift GCS VFD? Thanks
97
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
71
I have been trying to add a button to an HMI Panelview version 5.1 for a couple days. Each time I download I get no data in my buttons, only...
214