OMRON CQ1 and NT600S
Alex Pel
Feb 2004
Vancouver
145
Hello All.
I have no experience with Omron PLC and I am asked to find the problem in the working system. I have:
PLC – SYSMAC CQ1 CPU45-V1;
Soft - CX-PROGRAMMER 3.0;
HMI – NT600S (connected to PLC by the RS-232C method)
Soft – NT Support (can’t remember exact ver.)
I have uploaded the PLC program to CX-PROGRAMMER.
My problem is: - I couldn’t get on-line to NT600S.
Is it possible communication: PC (NT Support) -> CQ1 CPU45 - > NT600S?
Also I tried: PC (NT Support) -> NT600S? Unsuccessfully, may be wrong cable. Tomorrow I will try existing cable that connects CQ1 CPU45 - > NT600S.
I will be highly appreciated for any consideration
I think you can set the comms path to go though the processor, has been a while since I have done it, but from memory the function is there.
Just had a quick look, doesn't look like you can go through the NT support tool, you can with NS-Designer, or the new CX_designer.
The cable should be the same as the one you used to upload the PLC file.
With the NT screens however, you have to enable connection. I cannot find the manual on this procedure, but you press 2 corners of the NT screen, and then follow the menu system to enable transfer.
Hope this helps
Use this cable to connect PC (NT Support Tool) to NT600S.
Thanks a lot. I was away from my computer over weekend. “Pressing 2 corners” it is the news for me, think it will help. I have already made the cable; wiring taken from OMRON web site. It is the same as IO_Rack said except last two missing conductors. I’ll try tomorrow.
Thanks everybody. It works. I pressed two corners and went to transfer mode. After that successfully uploaded the HMI NT600S.
Has anyone done SMS messaging from an Omron CJ2J-CPU31 PLC? If so could you help please. Omron here in Oz have not had any experience doing this...
174
I have an old plc in the system I have, moxa nport was used to communicate with scada, I want to replace the plc with cj2m cpu33 and eliminate...
64
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
108
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
258
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
144