Hello - I have an Omron CQM1-cpu45 v1 set up with an AD041 input card.
Everthing works fine .... I need basic programming help
Thru reading the Omron manuals I am able to convert to inputs using the SCL instruction .... but not to an acceptable point.
I am able to convert the inputs but to a limited amout (30H to 0FD0H) to 0 to 100.
What i would like is to convert the input to 0 to 300 Degrees F with the most resolution possible, maybe 0.0 to 300.0 (or 0 to 3000) but i cant seem to understand the BCD math involved. can anyone help, any info or demo would help - I am used to reverse engineering so .....
Can you provide more information on your temperature transmitter?
What type of output? Overall temperature range?
This may point us in the right direction.
Temp transmitter : 4 to 20 mAmps for 0 to 300 Degrees F, but I would rather have a decimal value for Degrees C of -18 to 149 Degrees C
Strike 1, same question different explanation.
Ok, I've tried the SCL(66) instruction - works great.
I used Analogue input 1 - memory IR0001, scaled it like the example in the OMRON site, for 4 to 20 mAmps - im getting a result of 0 to 100 (decimal)
DM100= 0000
DM101= 0030
Dm102= 0100
DM103= 4048
I tried to change the scaling to 0 to 150 for an input of 4 to 20 mAmps
works great !!!
DM100= 0000
DM101= 0030
Dm102= 0150
DM103= 4048
But then i tried changing the scaling to 0 to 300 for an input of 4 to 20 mAmps - but the SCL result frezzes at ''&0''
DM100= 0000
DM101= 0030
DM102= 0300
DM103= 4048
What I would REALY like is to scale the input to 0 to 3000 but I seem to have hit the limits of SCL instruction. or I'm not understanding this math correctly)
I cannot seem to find detailed information on the OMRON instructions, what i have found is very limited.
The white paper for the SCL instruction says limits of 0000 or 9999 for the resullts (normal for 16 bit BCD)
Hi! Has someone a pinout and/or wiring diagram for an old CQM1-CIF02 cable? Thanks!
1,911
Hi; I have a DUPONT brand machine having OMRON PLC CQM1-CPU21-E. I have CX Programmer installed in my Laptop having W1indow10. I want to go...
3,629
Dear All, Does anybody knows Omron CQM1 0ch Module details?? or manual i try to search but cant find manual or complete order code if this...
2,382
Hi, I've been asked what is involved to upgrade and old CQM1-21 Omron PLC to a CJ2M. I have the old file with an extension of .cdm and searches...
1,589
Hi Everybody I have a very old CQM1 CPU21 Without memory cassette. I´m trying to set up protection UM, but I can´t, the following warning "Error...
3,318