omron plc
aliehghaghi
Oct 2006
tabriz
I have omron PLC type as cpm2c.I have problem with it.sometimes plc goes to stop and occur I/O bus error in plc.I use cx-programmer software.can anybody help me how can I solve this problem.
thanks
possible causes are communication losses to your other devices the CX_programmer should report which device is dropping out if its on a backplane Omron has some unreliability on the backplanes but if its on communication cables one could be faulty. What exactly do you mena when you say the PLC goes to stop? when you disconnect power to it??
HI moredad
when I say plc goes to stop run led on plc unlit and alarm led lit.
ann when i connect to plc in cx-programmer alarm logs I/O bus error massage occur.this problem happens sometimes when I power off after 5 minute plc go to run mode and plc work correctly but after 5 or 6 hours plc go to stop again.and when power off and after 5 minute on plc go to run mode.when I power on after power off without delay plc doesnot go to run mode.I have to wait some minutes
thanks
aliehghaghi said:
HI moredad
thanks
IMHO, this definately sounds like an over heating problem. I agree with Mordred. Are the expansion modules warm? What type of environment is this unit in? Have you tried to reseat any modules on the backplane? Post what you have already tried to do to fix the problem or investigate it. Might help us eleminate some issues.
HI craig
The envirement that plc works is an electrical cabinet in chemistry laboratory.there is not warm and any unit is not warm.at first I think this problem occured from poor connection in backplane bus. I opened all modules and fixed them and assemeled again.but this problem wasnot solved.I think there is problem in cpu module is it possible?
regard
HI craig
regard
Anything is possible. Do you have spare parts available? If yes try firstswapping out the backplane. If no result, change out the power supply and so on. Maybe someone with better suggestions will come along but until then check on available parts so that you can continue to move forward towards a solution.
Pretty hard to swap out the backplane - it is a shoebox PLC. I would be taking the whole lot to my Omron repair centre for testing.
I gather you need to wait several minutes before you can resart the PLC after it shuts down? if so then I agree with BobB on sending the unit to Omron and replacing it if so then it does sound like overheating on the CPU itself. If you have a temperature gun try seeing if their is any rise in temperature
I see what your saying BOBC after looking the type of connections and units involved try replacing the power supply module first also make sure you've got solid connections between the expansion units one other remote possibility is that the chemical fumes in the lab may be causing extra corrosion on the connection pins creating a high resistance I would try cleaning all the pins between modules. Also inspect the traces if you can get to them some chemical fumes can break down the epoxy coating and traces will usually show some form of discoloration
Hi my dear friends
tomorrow I clean the back plane connectin.If I get result it is good if not I try some other checks.I thank for your good suggestion for fixing this problem but I want you do not take me alone and I always looking forward to hearing you.
Best regards
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
136
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
121
Our plant manger/my boss wants each line to display the takt time above the line. I am trying to research the cheapest way to do this. Our plant...
188
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
109
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
217