Omron/siemens
aleb2
Nov 2003
I should read data from 14 OMRON E5CN termoregulators with a SIEMENS MP270;
I think one way could be through a PLC with 2 serial interfaces, one for MP270 and one for termoregulators' net (rs485) but i don't know which is the protocol to used for comunicate with these termoregulators
Can anybody help me please
Thank you
Hi aleb2.
You can select the OMRON Hostlink/Multilink protocol on the MP270 panel.
Unfortunately, you are not allowed to select RS485, only RS232 or RS422. This could indicate that multiple connections on the same port is not possible.
On the other hand, Win CC Flexible doesnt complain when I try to insert several connections on the IF1B port with RS422 set. So it could be that it is RS422 with Master/slave relation between the panel and the controllers. In that case it could work.
As you can guess I am not an expert in Omron or Hostlink/Multilink. I find out of the above by just trying to setup multiple connections via Hostlink/Multilink on an MP270 in Win CC Flexible.
edit: Of course, the above assumes that the controllers support Hostlink/Multilink.
You could investigate which protcols are available.
I have just skimmed that manual. It looks like aleb2 is out of luck.
The only mentioned protocol is CompoWay/F.
No Siemens panel supports this protocol directly.
Solutions:
1. Change the panel to one that supports CompoWay/F.
2. Change the controllers to ones that supports one of the MP270's supported protocols.
3. create a Protool or Win CC Flexible RT application on a PC, and to make the connection via an OPC server that supports CompoWay/F. OMRON has one called "CX-ServerOPC".
about point n.2: changing plc for example siemens CPU 214XP Which have no problem with MP270,but what about reading termoregulators data?
With "controller" I really meant the "termoregulators" that you were referring to.
So option 2 is to exchange the Omron E5CN controller with a type that supports one of the protocols that the MP270 supports.
There are many possible solutions. It depends on what is most important to you.
If the E5CN is absolutely required, then go for option 1.
If the MP270 is absolutely required, then go for option 2.
If the E5CN is absolutely required, but you also want to keep your HMI on a Siemens platform, then go for option 3.
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
291
I want to connect a S7-315 cpu to an Omron CJ2M via Ethernet I/P and transfer mainly bit data ie. turn an Omron output on from the S7-315 or turn...
2,491
We recently created a channel on YouTube about PLC Onron Training and the others . I am very happy to Share to the community...
1,943
I am looking for addressing difference between Omron and SIEMENS. In this Ladder netwoks has W10.00 address.This is a Omron ladder. I want to know...
9,333
Hello Experts, Anyone can help me how to configure the CX-Programmer to link a communication into Siemens MP277 touch screen. Any help is...
1,939