automatic Member A Join Date Aug 2004 Posts 136 Oct 1, 2004 #1 Why doesn't this work? I am trying to run the XFER command on a CS1 and it's not transferring the data. The PLC is in RUN mode. Last edited: Oct 1, 2004
Why doesn't this work? I am trying to run the XFER command on a CS1 and it's not transferring the data. The PLC is in RUN mode.
automatic Member OP A Join Date Aug 2004 Posts 136 Oct 1, 2004 #2 Found out the error. I should have been using &1 to specify number of words instead of 1.
Jay Anthony Member Join Date Apr 2002 Location Dallas, TX Posts 645 Oct 1, 2004 #3 When you use "1" with out a prefix qualifier of & or #, you are specifing the contents of a CIO word 1.
When you use "1" with out a prefix qualifier of & or #, you are specifing the contents of a CIO word 1.