Omronc200hs-connect to NEc barcode scanner

GanShan

Member
Join Date
Jan 2006
Location
Singapore
Posts
7
CAn any one please help me .. How to use a LK201 -v unit with an C200HS Omron plc ..to receive data from a NEc barcode scanner ?
BArcode scanner is 9 pin RS232C port and LK201 -V 25 pin rs232 , where to get pin config for lk201 , and any example program ...
please help
 
Sorry, the LK201 unit will only communicate Hostlink. Only option to connect a barcode reader to this cpu would be an ASCII/BASIC module.

It might be worth thinking about upgrading the processor to a CS1. You could reuse the IO modules and the barcode scanner could connect to the RS232 port on the cpu.

Hope this will help.
 