One for the old-timers
Steve Bailey
Apr 2002
The boondocks of Western Massachusetts USA
8,593
Sherman, fire up the wayback machine!
Is there anyone on the forum with experience with a redundant GE Series Six system? A site that has one (installed in 1986) has been experiencing intermittent problems the CPU dropping out of run. If the backup CPU is still running the transfer to it happens OK, but both CPUs are prone to dropping out. They can restart the PLC using the keyswitch.
The system has been out of service for several months although not powered down. The batteries are all good, at least as far as the battery LEDs are concerned.
I have some thoughts on which modules to start replacing first, but I'm wondering if there is anyone else out there who remembers these beasts. Rootboy, I'm talking about you!
TWS, I have all the relevant manuals. Thank you.
AKAHammer, I would not be surprised to find that the CPUs are stopping due to a watchdog timeout. But the programs have not changed between now and when they were running correctly.
So the question becomes what's the cause of the additional time per program scan. If it's because the redundancy controller is taking additional time to exchange data between the primary and the backup, then which module in the RPU should I replace? I was hoping there might be someone among the forum members who remembers the ways these systems fail.
Just a thought, probably nothing.
are the plc's tied together in the same panel?
are they connected to an ethernet switch?
have you tried to reseat the connections between the two systems, the cpu to the backplane, the i/o cards?
in regards to the reseat question, i have had this issue with AB plc's in the past due to dirty connections.
james
Both PLCs are in the same panel along with with the redundancy switch.
No ethernet involved. This system was commissioned in 1986.
Reseating the modules was one of my first suggestions to the site. That has helped in many Series Six systems.
The last one of these that I worked on was on a cardboard line, random faults and lockups.
After changing out all the electrolytic caps to no avail, I pulled all the cards and took an eraser to the contacts. Problem solved.
I am looking to get an AB series 1774 (PLC1) from the 1970's up and running. I have all the parts, and it powers up just fine without errors if I...
2,332
A
Is there anyone out there that can explain me what the different types of timers on the Westinghouse PC1100 plc are? (TT, TS)
3,555
This is admittedly a pretty obscure problem, but maybe someone else has run into it, or at least something similar. For reasons I won't get into...
138
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
235
Has anyone found a way to convert/replace/update the firmware on old Parker TS80xx series HMIs (i.e. TS8010, TS8006, etc) to accept Crimson...
100