OT: UL489 Circuit Breakers
kbcombs
Apr 2005
Muncie, IN
47
Do DIN rail mounted UL489 rated circuit breakers with a voltage rating above 240VAC exist? I have looked everywhere and can't find anything. Everything I find is only rated at or below 240VAC. Looking for something like the SquareD Multi9 series. Maybe I am looking at this wrong. I need a 2-pole breaker for the primary of a 480V pri/120V sec transformer. The main circuit breaker is UL489 MCCB @ 125A. Do I need to have a UL489 rated circuit breaker for the primary of the transformer? Any advice appreciated.
Thanks,
Kyle
If you are building a control panel for submittal to UL then you can probably get by using "recognized" rather than "listed" components. But watch out, many DIN rail breakers are only rated for "grounded wye" distribution systems.
From the Square D FAQ website - UL1077 Supplementary protectors are intended to provide equipment protection within appliances or other electrical equipment where UL 489 branch or feeder protection either is not required or is supplied by an appropriate UL489 listed device. Such equipment might include control transformers and electronic loads.
First of all, if you are protecting a branch circuit you need a UL 489 CB. It doesn't matter whether the entire panel is UL or not.
The AB 1489 series information specifies 480Y. Everywhere it references UL is uses this notation so I would assume that it is only good for 480Y installations.
Here is another thing to consider:
The Bulletin 1489 circuit breakers are "non 100 percent rated" as defined by UL 489, para 7.1.4.2. As such, the circuit breaker's rating
should be loaded to no more than 80% if used with continuous loads.
We represent the Moeller FAZ circuit breakers which are also UL 489 but only in single pole configurations and only for 240 VAC. I'm told they are coming out w/ 2 & 3 pole configurations and also 480V (no word on wheather the Y restriction will be there or not) soon.
UL489 lists breakers for specific voltages. Very few new designs of breakers are being listed for use on 480V ungrounded systems.
DIN rail breakers usually do not have enough "lug to panel clearance" to allow their use on voltages above 350V
I also thougt that there was an out for UL recognized branch circuit protectors, but in the latest revison (September 1, 2005) I can not seem to find it in the Supplement SA. It looks to me that all circuit protection must be UL listed, except for exceptions like semiconductor fuses as recomended by drives mfg and a couple of other narrow allowances for recognized circuit protection.
Darren
It is really confusing for me where to use UL1077 supplementary protector or UL489 brach circuit protection. For example what happens when the...
1,962
Does anyone have any recommendations for Electronic Circuit Breakers with 0V Terminals built-in and Fieldbus (IO-LINK, MODBUS TCP, EtherNet/IP?)...
206
Hello everyone, I'm having trouble selecting the right circuit breakers for the "line side" of my VFD. The common advice is to check the...
21
1,437
Hi everyone: we have Baumuller AC drive BM4463 300A 160KW, it drives Baumuller AC motor DST2-315BO54W-020-5-A (90KW;RPM 200; 365V; 215A;83Hz)...
370
Hi all, I'm working on a safety circuit and had some question about fusing. Incoming supply - 120V/15A Power supply - PSL-24-060...
611