PACsystems I/O mapping ALG628 card
Jan 2020
Orange, CT
I am a new engineer just graduated and have been tasked with 'documenting a gate station's I/O and functions'. I work for a large utility and these are Gas facilities. Mind you I hadn't the foggiest idea what that even meant 3 months ago and they haven't provided any training but I dove into Machine Edition and I think for most cards I can do a variable dump and between that and the terminal info get most of what I need - which is the Analog and Digital inputs and outputs and variables.
Except for the ALG628 cards. The variable dump for this one station, for instance, shows 4 variables of type AI_ALG628 and me has only channel 1 and 2 enabled. The 4 variables InPressure_Raw and Metering.InletPressure and OutPressure_Raw and Regulation.Outlet Pressure - so I feel these are actually just two instances each of two channels.
My question is: How do I know which variable corresponds to which channel?
Take a look at the hardware configuration for the module. It requires eight 32-bit Floating point variables for the eight channels plus four more 16-bit words for the HART data.
If it turns out that it is configured for addressed variables, then the addresses will be %AI memory. Each %AI memory location is a 16-bit word. A 32-bit floating point value will utilize two consecutive %AI addresses.
If the starting address for the module is %AI0017, then channel 1 will occupy %AI0017 and %AI0018, channel 2 will occupy %AI0019 and %AI0020, etc.
Yes I got that part - in this case the Channel Value Reference Address is %AI00901 so its 901 and 2 for channel 1 and 903 and 4 for channel 2. And I actually just found that in the variables window if I get the properties for these variables they are structured types that include an int for channel - so that solves my own question.
Don't quite have my head around HART yet. I get that its carrying both digital and analog info but what exactly is contained in those 4 words?
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
113
I have a possible application where an existing RX3i processor will need to get ASCII data over serial from a device (and no, I have no other...
2,627
Hi ALL, In the Rx3i controller fault table-the following fault keeps coming-up "0.4-LAN System-software fault: resuming" Error Code: 402...
9,352
Hello everyone. I'd like to give you a bit of background on me to start off. I've been working in control systems integration for 10 years...
2,688
All, Has anyone come across this new plc from GE fanuc? The vendor's brochures are quite impressive (as usual) ... but I have not knowledge of any...
1,709