Good morning all, programming a Panelview 800, I have a maintained push button programmed on screen 1. I copied and pasted it to screen 2. Could you please explain to me how to tie these push buttons together so when activated on screen 1 it's activated on screen 2. As of now, if activated on Screen 1 Screen 2 button is in inactivated state. The write tags are identical.
 
Check the Indicator Tag. You likely want this to be the same tag as your write unless you have some PLC output you would prefer to see as feedback that the button pressed worked.
 