PanelView 800 / Compactlogix L24ER

Holmux

Lifetime Supporting Member
Join Date
Oct 2013
Location
Aalborg
Posts
279
Dear All

I hope you can help me here :)

Trying to connect a Panelview 800 to a compactlogix L24ER, not as straight forward as I expected, I have this CCW software is this all I need ?

I see the panel OK from the CCW software, but have trouble linking my tags to the PLC, do I need to step up and get a different software packet ?

Thanks
/Holm
 
Hi George

Thanks for the help, this little thing is bugging me :)

I am using the Compactlogix protocol, I am using the same Gateway and network mask PLC: 192.168.0.20, Panelview: 192.168.0.21, Gate 192.168.0.1

After setting up the PLC with address 192.168.0.21,1,0 and go and what to make a tag, it tells me "no controller is selected" hmmm. what am I doing wrong.

Regards
Holm
 
I had the same issue when I first used the Panelview 800. In the address field of the tag editor use your tag name Not the PLC address.
 
Working :)

Just had to get my head around the logic of this tag editor, very sensitiv beast :)

Thanks for the help :geek:
 
I'm glad you're sorted, but what exactly was the problem/fix? All of the necessary step, I had thought, for creating controller tags in CCW, were explained in my linked thread.

I notice you've said...

Holmux said:
...PLC: 192.168.0.20, Panelview: 192.168.0.21, Gate 192.168.0.1

After setting up the PLC with address 192.168.0.21,1,0

Was that just a typo error? The PLC is .20 or .21? A little mistake like that in CCW could could have you head scratching, for a while.

G.
 
Hi George

Everything was setup perfect, but if I was writing the tag name instead of copy paste from the controller, you get this error message that there is no controller selected and I kept going back to fix the controller setup, going a bit around in cirkels :)

Well a good day is when you learn something new :)

Thanks again
/Holm
 
The Perpetual Silver Lining...

Holmux said:
...going a bit around in cirkels...Well a good day is when you learn something new...

Remember, the most apparently embarrassing mistakes are the ones you are least likely to forget.

Trust me, I did not learn the minutae of my craft by being perfect, first time, every time. It takes years to hone one's stupidity into a finely tuned "hardway" learning machine. Never doubt one's ability to reach new levels of "stoopid".

CCW is one hell of a tester and improver of said "hardway" learning machine.

G.
 

Similar Topics

I'm trying to convert an old panelview 600 application to the 800 and I'd like to keep the current serial comms configuration instead of adding...
Replies
1
Views
614
Hello everyone, I hope you are well, I have a CompactLogix 5380 PLC (5069-L310ERM) and I would like to communicate with a PanelView 800 HMI...
Replies
0
Views
732
Hi, I am currently working on a project which involves PanelView Plus 800 as HMI and compactlogix 1769 30ER controller. There are 400 tags that...
Replies
9
Views
4,631
Hi experts, I have Panelview 800 Teriminal (version 4.012) connected to 5370 compactlogix L2 controller(1769-L24ER-QBFC1B). Through Ethernet...
Replies
6
Views
16,541
As the title says, I'm using CCW with a PV800 (and Micro850). I've made a scheduler in which a user can choose a month, day (1-31), hour (0-23)...
Replies
15
Views
554
Back
Top Bottom