Thanks a million. I do not have techconnect, but I will find it somewhere. I have programmed RSLogix as:
O:4/6 where the 4 refers to slot 4 and the 6 is the particular output. So, from your example, would I need to re-address the I/O in RSLogix or just in the PV Tags?
Thanks again,
David
just in the PV Tags...
Post a screenshot of the Input and Output data tables and I can explain it from that image.
Crop the image as narrow as reasonable and post it as a jpg.
I am on the road, without access to RSLogix or I would give and example.
From my understanding of the technote, you simply count
rows (words) after
word I:0.0 until you get to your expansion card, and program the PVC with that number instead of the value which is used in RSLogix500. So, O:4.0/x might become O:6.0/x but only in the Panelview, NOT in the Micrologix or RSLogix500...
The technote gave two examples with different word offsets. I, having never used the 1400, don't know if that is because there are different base models with different onboard I/O count, or if it's a digital vs. analog base unit that makes the difference.
IIRC the 2nd example they gave had a word address of I:9.0
I think its a $hame that a/b thinks that information should not be available to everyone...hopefully it is (somewhere) in one or more of their manuals already.
And on a sidenote, it is my practice, and I am sure others would agree:
it is a good practice to never address real I/O with an HMI. It will always be beneficial to be able to remap it...on the fly...without interrupting the HMI. It will make your code constructs more portable, give you the chance to optimize communication efficiency, and get around weird problems like this one, but the main reason is trust. I never want to control I/O directly with anything but the PLC which is quite trustworthy and not subject to driver flaws and comms losses. In my opinion, it is always better to map them in the PLC, bit by bit to internal addresses that fall in line with your existing communications design for the HMI data.
Continuous blocks of data on each HMI screen are your friend.