PanelView connection to Multistate button
realolman
Mar 2009
here
584
In FactoryTalk ME I configured a PLC COmpact Logix In the RSLinx Communication setup to be called "checker" with a shortcut
It verifies that checker is assigned to the desired PLC on the tree.. I have runtime the same as the design time
At this point I have one multistate button on the MAIN screen and it also has a shutdown button
I want the button to be connected to the tag "solenoid_enabled" in the "checker"PLC program
In the connection tab of the multistate button, exactly what syntax do I use to make the connection
I have it as {checker:solenoid_enabled} , but that doesn't seem to work ... and I can't even read what it says for errors in the PanelViewPlus 600 screen... Initially, the button comes up with a question mark on it
I want to get one button going before I do anything that amounts to anything
a little help , please... thank you
Have you got the offline PLC program.
You can add a PLC file to the Enterprise shortcut area, where you will be able to browse directly to your PLC.
A lot of the structure depends where the tag is in your PLC.
I assume you are using RS Logix 5000, since you have a tag called solenoid_enable.
If you are using it as a controller tag it would look something like this : {[KP]Sterile_Air_Pressure}
Where KP is the shortcut setup in Enterprise, and Sterile_Air_Pressure is the tag.
If you were going to a program tag it would look like this :
{::[HPS_PLC]Program:MainProgram.AV0405.Man_Req}
Where HPS_PLC is the shortcut, MainProgram is the program it sits in and AV0405.Man_Req is the tag.
Hope this helps.
Cheers
Mark
thank you very much I think my problem is a syntax one and what you have posted looks like it should solve that
It is controller tags
What do you mean by adding a file to the Enterprise shortcut area and browsing the PLC ... that sounds good
again thank you.
Hello, I have a machine with a 1756-L72 Controllogix PLC and 1756-EN2T network card, and PanelView Plus 7 HMI. I am using RSLogix V20.05.00...
922
My PVP7 (performance) Hmi keeps losing connection to plc. Plc is L33ER v31.011, Switch is Stratix 5400, also on the network are two EIP leak test...
1,748
Good Evening , I have a large machine that has 2 - Rockwell 1783-US16T unmanaged switches. I have about 17 Powerflex 525 drives that keep...
2,619
Hi everyone, I am trying to figure out how to get a Panelview 800 (Ver 5.012) to talk to a SLC 5/04 through a ControlLogix bridge. The bridge...
2,600
Hi, I am currently working on a project which involves PanelView Plus 800 as HMI and compactlogix 1769 30ER controller. There are 400 tags that...
4,603