Hello,
I am able to use the ME transfer utility (and see the panelviews in Rslinx) when I connect to an Panelview Plus Compact 600 271PC-T6C20D. When I try to connect to a Panelview Plus 600 (appears to be a newer style-clear plastic cover over comm/fault)2711PC-T6C20D8, I am unable to see it in Rslinx or the transfer utility. I have updated Studio to 8.2, and have updated the transfer utility... any ideas on what my issue may be? I've tried connecting to a few of the "newer style" with the same result...
Thanks,
Keith
I am not sure if this is a fix for you since I have not upgraded to FTV Studio 8.2 yet, but for version 8.0 and 8.1 we had issues with RSLinx Enterprise.
Try doing a REPAIR of your RSLinx Enterprise install, or even a un-install/re-install.
Also check your windows Services and change from Automatic to Manual that way it is only called to run when you launch an RA application that need the RSLinx Enterprise.
Best of Luck...
KuulKuum
It ended up being the Ethernet driver not being loaded in on the panelview plus. I didn't realize you could load a file and prevent future communication with it (until you go into the HMI settings to set it back up).
Thanks for the advice.
can anyone help with trying to connect a panelview plus 7 to a pc i made a ip address for the panel view i ping it from my pc and its seeing it...
20
3,581
Hi again, I have many times used RSLinx to connect to PLC's with the DF-1 serial driver and a USB-RS232 adaptor. No problems. Now I'm trying to...
4,383
Hi, guys, how’s going? We have one SIMOTION D435 machine. D435, PLC and HMI are connected via Ethernet cable: D435 X150 (IP:192.168.214。。。) PLC...
4,368
I have been able to connect the computer to the Panelview, I cannot seem to get commication right to the PLC. Can someone help me with this?
4,177
I am new to using PLCs and HMIs. I have an Allen Bradley CompactLogix L2 controller and a PanelView Plus 7 HMI (both new units). I've connected...
14,334