Hello, I have two 12" PanelView Plus 6 that runs exact same application. Is there a way to monitor status for both PanelViews?
I know there is a heart connection in global connection but since I have two PanelViews running same application it will be same tag. So I will not know if one PanelView fails.
Use the terminal IP address.
You could solve it a few different ways; here's one.
Use the activeX MEIPInfo to read the last number of the IP address (IPOctet4), on the startup display.
Use the Remote Display Number in global connections to open a pop-up (that never closes) of the same number. Ex. IP address is 192.168.1.174 and it would open display number 174.
On the pop-up display use the activeX MEMacro10 to write any heartbeat you want to your PLC.
You will need a pop-up display for each IP address, and each pop-up is coded to write to different tags in the PLC.
It will be a pain if you want to change or add IP addresses as you will have to update your project. But at least you only have 1 project to maintain that works for any terminal.
Getting fancy, you could even hide/show different screens based on the IP address. That lets you have just 1 project for different panel stations; which makes maintenance easier as there is only 1 project file. No need to worry about getting the correct file for a specific station.
Hi, Rockwell beginner here, so I have been trying to set up an HMI Screen in Panelview PLus 1000, which would tell the customer if a link is...
5,636
I am using a Micrologix 1400 talking to a Panelview Plus 400 with firmware 5.10 and using FactoryTalk View Studio - Machine Edition. When one...
3,634
I’m running short on time to complete this project (retirement looming), so thought I’d ask here hopefully save me some research time. I’m...
133
196
Replaced overlay and glass in HMI but now I can not calibrate the touch screen any suggestions.
91