If it was noise somewhere else in the duct bank, then why would the problem only exist when the PV+ is connected.
That is a good question but I think that the noise could be affecting
the network only when there is a load on the section of DH+
where PV+ is connected.
A-B likes to preach about the need to have at least 6 feet of cable between devices. If the cable between the PV+ and the SLC 5/04 in our panel is less than 6 feet in lenght, could we be getting some reflections in the signal?? Just graspong at straws, but I'll throw that out there.....
I usually leave 10 Feet coiled up in the panel just to be on the safe side.
I also had a recent problem with Remote I/O which works approximately the same way as DH+. We had blue hose in a duct next to cables feeding
plating rectifiers and that was enough to cause a problem. We had to
re-route the blue hose.
I suggest that you run a parallel blue hose cable next to the duct outside and away from anything that might produce noise.
Then connect this cable instead of the one inside the duct.
Blue hose is not that expensive and you can always re-use it.
This way you will eliminate one possible source of noise.
If that does not help I suggest that you lower your line end termination resistors to 75 Ohms.
There is another way of reducing the traffic on the DH+.
Instead of polling your RSView tags you could
do unsolicited messages and send the data up based on an event.
However I do think that your problem is hardware related.