I was just working on a machine that uses devicenet. how to select baud rate for
DeviceNet driver in RSLinx when using pass-through connection?
It seam to be impossible to use any other rate than 125kbps. Is this true?
 
If this is a ControlLogix rack you do not configure the baud rate for the passthrough connection. Now if you are wanting to set the baud rate for the scanner (1756-SDN), then that is a different issue. You set that value from inside RSNetworx or using the node commisioning wizard.

Darren
 
What you are seeing is a quirk of the 1771-SDNPT and 1747-SDNPT drivers. They are always labeled "125 kb" in the RSLinx driver configuration window, no matter what speed the 1747-SDN scanner is itself running at.

The pass-through drivers are so painfully slow that I try not to use them unless there's absolutely no choice. The 1770-KFD is expensive, but necessary.
 

Similar Topics

Hi all, I have multiple Allen Bradley SLC5 PLCs on my site, with most of them having a DeviceNet card installed. Each PLC also has an Ethernet...
Replies
1
Views
2,385
Hi. I want to configure a pass through driver for devicenet with a slc 5/03 and devicenet scanner. I only have one node so I thought this would be...
Replies
7
Views
5,615
Till now we used SLC500 on our machines. I was able to setup devicenet by using pass through ethernet - devicenet, on SLC processors. I like to...
Replies
3
Views
3,425
I've been given a line that has several sysmac c200Hx PLCs. The First station Im trying to wrap my head around has a NS8 HMI. I'm using Cx-one...
Replies
2
Views
757
I am new to Rockwell stuff, have more experience with IDEC. I was handed a half completed project using a Micro820 and a Panelview 2711-T2T. There...
Replies
4
Views
2,018
Back
Top Bottom