Kataeb Member K Join Date Jan 2007 Location www.livelovelebanon.com Posts 636 Jan 17, 2018 #1 Kindly , in Siemens PCS7 , has anyone seen and solved this problem ? " Maximum length of code area reached (max. 64 Kbytes) "
Kindly , in Siemens PCS7 , has anyone seen and solved this problem ? " Maximum length of code area reached (max. 64 Kbytes) "
cardosocea Member C Join Date Nov 2016 Location Fields of corn Posts 2,651 Jan 17, 2018 #2 When did that error appeared? After what action?
JRW Member Join Date Jun 2002 Location South Carolina Posts 2,318 Jan 17, 2018 #3 Sounds like your exceeding the size of the FC,FB or OB your trying to download Technically the max is 65534 but..... Last edited: Jan 17, 2018
Sounds like your exceeding the size of the FC,FB or OB your trying to download Technically the max is 65534 but.....
Kataeb Member OP K Join Date Jan 2007 Location www.livelovelebanon.com Posts 636 Jan 18, 2018 #4 Turned out to be the FC50 exceeding the 63K. It was due to lot of blocks(not inserted in runtime group) in OB100, Thank you https://support.industry.siemens.co...n-the-cfc-charts-are-compiled-?dti=0&lc=en-WW
Turned out to be the FC50 exceeding the 63K. It was due to lot of blocks(not inserted in runtime group) in OB100, Thank you https://support.industry.siemens.co...n-the-cfc-charts-are-compiled-?dti=0&lc=en-WW