Hello,
I have a fault on a differential pressure transmitter of a fire water pump. Indeed, by measuring the voltage at the level of the transmitter; it was zero (0 VDC) instead of 24 VDC. We replaced replacing the 1715-IF16 board to which my transmitter was connected. By measuring again the voltage coming out of our PLC card, we found 19 VDC; and by connecting our differential pressure transmitter the voltage drops to zero.
Does any of you have any idea about the cause of this brutal tension? And can he have an idea about the cause of this defect in order to remedy it?
Thank you
Is it a two wire transmitter? Or is it a pressure switch?
What you describe is a sign that the pressure transmitter is shorted. Have you checked the connections to ground?
I've troubleshooted some of that 24VDC stuff before. A good method for me is to first take the wire off the card and check voltage. If it's 24 or more, then good, if not check what's going on with the card. Second, if it's good, put the wire back on and take the wire OFF the transmitter. Check voltage. If 24, then good, if not, check the wire for a pinch or a short. If good, replace wire on transmitter. If not good, then like cardosocea said, probably a bad transmitter or ground. Ground connections are important in 24V.
New to the ABpoint IO and have some experience with plcs but not that much. Anyway my question is why are these output cards flashing red? I am...
1,149
Hi Can anyone give us the name and part number of programming cable for AM1000 fire and gas panel. Thanks
1,022
I am using studio 5000 for the program. For some reason even when the ladder logic is completely true to fire the output, the output still will...
26
6,599
We are thing about installing temperature sensors in the area of some of our large hydraulic systems These sensors would monitor the temperatures...
3,522
Hi guys I'm working on this project: There's a Fire Alarm system installed in a plant that we want to communicate with using a CompactLogix L32E...
2,484