In our Controllogix Program there is a periodic task (for Modbus Communication from AB PLC to DCS), we got a communication problem. When checking ,we found there is 2 task overlap count happened although I see the scan time for the task (3.6 to 16.7) is very less than the period time(200 ms) as in the attachment. noticed the max. interval time(289ms) is more double the min. interval time(140ms)!!not clear why this difference?, Appreciate for any explanation of why this task overlap happened?? also why we loss communication to DCS when this overlap happened . the communication returned when we reset and click selecting (Disable Automatic output processing to reduce task overhead)..Please appreciate any explanation for this problem??
Hello everyone, I am new to PLCs, what will happen if I set the Period of a Periodic task lesser than its execution Time for ControlLogix...
1,687
I currently running a compact logix 1769-L33ER 20.11. I have a functioning periodic task that runs every 100ms, using rslogix 5000. This task is...
2,532
I've inherited a L61 that was installed last year and the memory usage is well into the red. There is only one continuous task with a scan time of...
3,783
Can this be done based on a pre-selected condition while the PLC is in Run mode? (Logix 5K V20 - Compactlogix L43 CPU)
17
5,311
Have you ever implemented an event driven periodic task in CLX? How'd you go about it? I have a task that needs to be executed at least every...
2,510