Hi all,
So I just converted an old dc drive and motor to a PF700 vector drive and vector motor. its all up and running except for the analog out to plc.
i have it set up to send drive current to the plc via 4-20Ma on analog output 1.
I am getting the signal to the plc but the signal is crosstalking to 3 other channels on the card giving me false readings on the card. pull one of the signal wires coming from the drive and the problem goes away.
do i need to tie drive 24vdc common to ground or something else like that?
The card is 1771-ife/c set up for differential current
the drive is 20BD052A3AYNAND0 ser. B, 480VAC, 52A, 40Hp
using pins 6 and 7 on drive for analog out 1
pram 340 bit 0 is set to 1
pram 342 is set to 2
pram 343 is set to 20Ma
pram 344 is set to 4Ma
any ideas would be great. this has a few of us stumped.
What you are describing, is called common mode noise when you read the manual for the IFE, and it appears to me, that the way to fix your problem is to buy a 4 to 20 ...4 to 20 isolator, Pheonix is popular in the US, here in NZ we use Intech isolators
Hello all, I am working on an old bagger that is giving a EUP fault which is undervoltage and intermittent. Electrical power cycles and gets the...
1,244
Hey guys, have any of ever seen a PF700 reset its parameters to factory default on its own while running? I don't think it is possible, but I had...
1,883
Hi, I am having trouble with a PowerFlex 700 drive in RSLogix 5000 version 20.11 in an L64. I have an ACD file for a heavily used PLC that is...
3,537
I have a really weird problem with an AB PF700 drive that only faults out with one specific product. Why it is weird is because it is a Port5 DPI...
2,391
I am using an AB PF700 VFD and a Contrologix processor. When using datalinks to change a parameter, if it is a configuration type parameter with...
1,068