PFLX525. Swap the power module only?
unsaint32
Oct 2012
minneapolis
365
After PFLX525 malfunction, someone installed 1/2HP drive, when the project needed 2HP drive. I think only difference between 1/2HP PFLX525 & 2HP PFLX525 is the power module. Please correct me if not so.
If so, can I just swap out the power module? In other words, can I take the control module off the 1/2HP drive power module then plug it into the 2HP drive power module? If I did that, do I need to do any configuration?
At the very least you would have to program the motor details.
I know on some of the other PowerFlex drives the drive size is on the Gate Driver Board (Power Interface Board), so I would be supprised if this drive was not the same.
Alan
Yes you can, the control modules are all the same, the power module is coded to tell the control module what you are plugging it into so that it changes the parameter ranges for size related issues. Back up your program first however.
So I have an interesting question. I work with sites that don't have controls tech's and wanted to know if its possible for a processor to be...
1,233
I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
1,039
I feel a little silly asking this, but can you “hot swap” a battery on a 1756-L55 processor?
1,243
I have a C-More HMI that changes my PLC String from "Machine Status" to "aMhcni etStasu" . There is an option with other objects that have string...
3,516
I want to know how to make a flip flop rung that will change states every scan. This is for a fast sequencer. Is there a special bit similar to a...
2,210