pid error on slc 505
stu
Aug 2005
England
783
Hi guys
I have had a problem twice now with a slc 505 having a fault light come on after the power has been turned off,
I connected to the plc as you do , went go to error it said invalid value pid, s:1/13 had a 1 in the box, ?
The only way to reset was to load the program back into slc,
Is there another way I could have reset the fault
Thanks stu
You would have to clear the error AND change the invalid value to something valid. You can clear the error with RSLogix500 software, or by cycling the keyswitch to program mode and then back to run mode, but if the invalid number is still there, it will immediately error again.
Can you zip and post your code? It sounds like it may need some polishing touches to prevent erroneous values from being entered in the PID block.
Hi Everyone, I am working on a project in Proworx NXT, and noticed something with some in service PID controllers. I have a Flow Controller...
1,425
Background: PLC AB 1756-L61 v13 redundant via SRMs I have a thermal refractory furnace which allows excess air to enter the process to quench the...
2,594
Hi I am using S7 1200 PLC . I want to use pid compact to control pressure trough manupulating the speed of motor using ACS850 vfd. The...
1,072
I recently needed to add a feature to a program which allows the operator to limit the output percent of a VFD controlled 2 HP pump motor. I...
3,338
I don,t know how to design a ladder to control operation of pneumatic valve with PID input?
2,958