Dear All,
I have an Allen Bradley PID question and appreciate if anyone can advice me here. Basically we have 4 heating profiles in a machine with PID control in the PLC.
We key in the setpoint from the Panel View, then the PID instruction will control the pulse of the heating profile through the relays.
All these 4 profiles had been working well all the while. Recently we tried to tuned the P and I parameter to get better performance. The 4 profiles work well, but suddenly one of the profile went out of control. We are unable to control the PID control variable output.
Please refer to the pictures. Pic 1-1 show the PID that is working normally.
We see can see the PV is close to the SP. And Output % is the right figure to control the output.
Pic 2-1 show the PID that doesn’t work well. The PV is far from the setpoint and the Output % is 100.
I had monitor the Controller Tag for the RTD input channels. All these 4 give me the correct values.
Hope there is anyone who can advice me. Lot of thanks! :)
some helpful hints:
a) When referring to pictures, please remember to post them.
b) Do a search of the forum for PID, you will most likely see some posts by Ron, who is generally accepted as the authority on teaching the finer points of PID (apologies to anyone who feels differently).
Also, when you post the pictures, please let us know if this is a PLC/5, SLC500, MicroLogix, or ControlLogix PLC, and if its a ControlLogix PLC, is it using PID or PIDE?
since you mentioned "Controller Tag" I'm guessing that you're working with a ControlLogix platform ...
when you post the pictures (trend graphs?) please also ZIP and post the program file (example: MYPROG.ACD) ...
I need help defining the PID instruction and all the elements, can you help me. Thanks
3,580
Hi I need help with tunning pid block for Allen Bradley’s PLC SLC500 and processor 5/03. Only for test how to use this instruction I download a...
4,597
Hello, there is anyone who have already used hpmont plc? now i am programming for that plc and have " pid autotuning is not working" issue. I have...
980
Hello, Speaking of PID Instuction in RSLogix. What is the difference between Both "Manual" and Software Manual" (.MO versus .SWM) modes and...
1,530