PID Loop RSLogix 5000
May 2015
Colorado
I am trying to adjust my PID loop: The process variable is % solids in water. The control Variable is % VFD pump speed.
The problem with the PID loop is that it only looks at pump speed for the high limit and low limit. I want it to also take into account pump flow for the limits. I would somehow like to program it to only be able to go down to a certain flow rate - the % VFD limits fluctuate, sometimes 0% is a much different flow than other times.
Would this be solved by using cascading PID loops?
I Still would like to get a little direction on this. The problem is my low limit on my control variable is only pump speed. I would like to have the PID also reference another variable for a low limit - pump flow. Is it possible to tie in two different limits into this?
Thank you.
I'd suggest looking at this:
http://literature.rockwellautomation.com/idc/groups/literature/documents/wp/logix-wp008_-en-p.pdf
It sounds like you want to do multiloop selection, namely control %solids with the constraint of satisfying some lower flow limt. This will involve 2 PIDEs, one for %solids, the other for flow. The output of each PIDE goes to one high-select block; the output of the high-select block goes to the VFD and also to the CVPrevious field of each PIDE. The setpoint of the flow PIDE is set at about the low flow limit for your process.
Look over the above, think about it, and ask followup questions as needed if you think this is the path to take.
Thanks for the suggestions.
"It sounds like you want to do multiloop selection, namely control %solids with the constraint of satisfying some lower flow limt. This will involve 2 PIDEs, one for %solids, the other for flow. The output of each PIDE goes to one high-select block; the output of the high-select block goes to the VFD and also to the CVPrevious field of each PIDE. The setpoint of the flow PIDE is set at about the low flow limit for your process. "
I am only familiar with ladder logic at this point. Is this method you describe above something that can be done with a standard PID?
I am using PID instruction in RS Logix 5000 with independent equation. I am confused about its tuning. Please somebody explain under listed...
4,946
I'm new to PLC's and am working on a practice program which includes a PID control for a steam valve used to control the temperature in a tank...
17
21,485
Is there any sample PLC code or code for sale that would control a constant ratio of four ingredients being mixed together? The code will pull...
15,701
I have a 4-20mA coming from a temperature transmitter. I need to create a PID loop to contol a steam valve. Using RS LOGIX 5/03 processor. I have...
7,821
Hello, I am attempting to tune a PID loop on a process. The process involves a valve with electronic actuator that has quite a high deadband...
2,234