drbitboy
Lifetime Supporting Member
P.S another option would be to write a few rungs to disable the PID on startup and keep the valve closed until it gets to, say, 10-20PSI below the setpoint, then open the valve to around where it will end up, which should be discoverable empirically, then let the PID start updating, assuming the instruction will have a bumpless transition.