Plc 5/10 1771 if15i
bigLee
Jun 2018
Florida
77
I have a working PLC 5/10 with 1771 16 channel analog input module. Currently has 4 direct 2 wire analog signals in. Just positive and negative landed on channels 0-3. 4 is common?
An instrument has changed from direct analog in signal to an internally powered 24vdc sourcing input.
My question is, do I need 250 ohm resistors between my input wires and/ or do I need to change a jumper for this channel on the module?
I'm not really familiar with these older cards. I know typically I can seperate the signals somehow before the input terminals so the positive analog signal is received onto the negative wire terminal at analog card.
Any insight is appreciated.
So, Are these inputs voltage or current inputs? If I remember right, those cards allowed you to set each 'pair' of inputs (0,1 2,3 4,5 etc...) to either voltage or current and differential or single ended. Bunch of options, best to grab the manual for the card.
It sounds like you have a 1771-IFE analog input module? Which is capable of 16 single ended analog inputs or 8 differential inputs. I have never used a resistor on these units, they have the resistance build in to the channel.
I think in single ended mode the channels are broken up into 4's for example 1,2,3,4 are channels 1-4, 5 is common, 6,7,8,9 are channels 5-8, 10 is common, and so on. in differential mode 1,2 is channel 1. 3,4 is channel 2. 5 is not used, and so on.
I advise downloading the manual, the channel setting jumpers are different depending on the series of the module. There is a series A, B, or C at least.
if it is the 1771-IFE, there are jumpers under the cover that are used to set the channels to either voltage or current. There is a guide printed on the card/circuit board, and it is straightforward.
A question was sent via PM this morning from a new member (Vince9521, from up in Timmins, Ontario) that I'm promoting to the main forum:
1,075
Hey everyone, Trying to bench test the I/O on a program that I converted from a PLC-5 processor to a ControlLogix processor but still using the...
21
6,520
These two RTD's are wired to channels 1 and 2 on a 1771-IR in a remote rack, communicating to a PLC-5/40 through an ASB. I believe that the RTD's...
1,965
Hello, I am in the process of migrating a PLC-5 system over to ControlLogix and could not find any equivalent modules to convert the 1771-ALX...
1,489
Hello, I am trying to create a network status map at a plant. I'm assuming the comm status bit of dnet nodes is in the BTR/BTW instruction that...
981