PLC 5-15 powers up in remote program mode

don1969

Member
Join Date
Jan 2005
Posts
9
I have a 1785-LT B PLC 5/15 processor that on power up starts up in remote program mode instead of remote run mode. The key switch is in remote. I have never seen this before, all our processors are set in remote mode and always start up in remote run mode. Any ideas? Thanks, Don.
 
get online and change the processor status to run,there is a drop down on the top left that at the moment will be in "remote".the key switch can be in either "remote" or "run".
 
If you have an EPROM stuck in the bottom of the processor it may be loading off the EPROM on start. In that case I think it will start in program mode.

Keith
 
Long time since I was in affairs with AB 5/15, but I recall that this is a DIP switch setting in the chassiss it self, if I still remember it is no 8.


Cheers
Hagos
 

Similar Topics

I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
38
kindly need to understand why can't upload the plc
Replies
2
Views
56
Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
Replies
3
Views
60
The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
11
Views
273
the conveyor can stop because of a safety sensor or safety switch. And also it can stop because of an object jam detector sensor. If the conveyor...
Replies
5
Views
197
Back
Top Bottom