plc 5 1771-il module
cbplc5
Jun 2018
wisconsin
I am doing a little self training and looking for some feedback. I have a plc 5 with a 1771-il module looking into some scaling issues with an input. I am looking at changing the raw min and raw max of the BTW of the input and would like to know that when I accept edits on this change a pop up is displayed "do you want to download the configuration to the module". If I download the change will this stop the process?
Welcome to the Forum!
You do not have to edit (and you definitely should not) any Block Transfers, Data Table and/or logic in order to adjust any 1771 analog signal scaling.
Use the RSLogix 5 I/O Configuration applet which will provide you with all the available 'adjustable' settings for the analog module's channels; just type in the value(s) and hit the Enter key.
If the respective module's BTW is being processed every scan the new scaling will be implemented immediately; if the BTW is triggered only at Power-Up time you might need to add an XIC of an unused memory bit in parallel with the Power-Up bit and make it '1' then '0' with the PLC5 in Run mode; you could Delete the instruction upon finishing the tweaking in order to prevent someone else to inadvertently change the configuration.
A question was sent via PM this morning from a new member (Vince9521, from up in Timmins, Ontario) that I'm promoting to the main forum:
1,077
Hey everyone, Trying to bench test the I/O on a program that I converted from a PLC-5 processor to a ControlLogix processor but still using the...
21
6,521
Hi, We have a customer using PLC-5 system with RIO. From what they complain is the slow speed of the PLC DI (normal), thus they wanted to get...
17
10,455
These two RTD's are wired to channels 1 and 2 on a 1771-IR in a remote rack, communicating to a PLC-5/40 through an ASB. I believe that the RTD's...
1,968
Hello, I am in the process of migrating a PLC-5 system over to ControlLogix and could not find any equivalent modules to convert the 1771-ALX...
1,491