PLC 5/40E with Ethernet Flex I/O?
eleall
Jan 2006
Medellín
Can i do that??
I have been searching but i just found that i can do that but with a RIO Flex IO using the 1794-ASB.
Is there a way to make the communication using the 1794-AENT?
What's the reason that you don't use the RIO option?
It's so easy and quick to use.
If you realy want to have ethernet for remote IO, you have to add a "master" on the ethernet. Here in the factory we use a CompactLogix PLC as Ethernet Master in combination with a PLC5/40E like you have.
Regards
Jack
The designer sent me the architecture using a PLC-5 with ethernet Flex IO and i had doubt about if is supported and your answers confirmed that. Now i sent the mistake to the designer and now he has to see what is he going to do, if use a CompactLogix master or maybe the Rio module. I rather the master architecture with the CompactLogix, the rio communication is kind of old.
The RIO option is old, but very easy, and very quick.
I would have a RIO scanner on the CompactLogix, but this is only an option for ControlLogix.
Now I've to work around the **** of IPadresses and MSG instructions.:confused:
My choice would be RIO...
Goodluck
I dont know if he is going to choose RIO because the distances between the Flex IO and the PLC (a little bit long, dont know exactly the distances between them :S), also, does'nt the PLC-5 CPU need something additional like a connector or something to be used with the RIO??
What is the reason for this project?
I ask because you may be better served with other options that we could help you with.
Distance shouldn't be a problem, RIO is good for considerably longer distance than standard Ethernet. The 5/40E should have Channels that can be used for RIO etc. It is a 3 Pin Connector, and should be on the front of the CPU.
Stu.....
Stu's right on: RIO can run 10,000 feet at 57.6 kb/s and 2,500 feet at 230.4 kb/s.
The PLC-5/40E has a daughtercard with one DH+ and one RIO port, plus Channel 0 for serial and Channel 2 for Ethernet.
The other alternative for I/O and peer-to-peer communications with PLC-5 controllers is ControlNet (the PLC-5C15 versions).
But the PLC-5 definitely, positively, certainly does not support I/O on Ethernet.
hi, I observed that PLC 5/40E is not observing its subnet configuration. If i put IP address of range 192.x.x.x it assumes its c class and if I...
1,349
How do I find the ip address of the processor? I don't see it written anywhere! Thanks in Advance.
1,521
Hi All, I am working on a project where I am integrating two different PLCs on a single network. I want to know how can I access I/O points of...
3,487
okay i have a plc 5/40e that is programmed from a scada running rs logix 5 ver(5.2.3) we programed the ip address for the plc with DH+ for channel...
3,284
G
I have a PLC 5/40E that I would like to put on an Ethernet network. What do I use to go from the 15 pin Channel 2 to RJ45 connection? Where can I...
2,462