PLC-5 LED's
ceilingwalker
Mar 2010
Phoenix, AZ
1,588
Good day all. I wanted to know if the LED's on the front of a a 1771-ID should light up for a specific terminal, if the proper voltage is put across it. I know on the SLC500 Input module whether it is programmed or not, if it sees 110V, it will light. I have three inputs that have 120V and the LED's are not lit. Other LED's on the same module are lit, with the same voltage. Also, please, how do I check IO configuration on a PLC-5? The IO config doesn't give a nice little list of the components, like the SLC500. Thank you.
The 1771-ID is an Isolated Input Card, and has a seperate Neutral (L2) Connection for each Input on the even Terminals. Are these connected for each Input?
http://literature.rockwellautomation.com/idc/groups/literature/documents/td/1771-td019_-en-p.pdf
Stu....
On this project, the operator's asked me to add an LED onto the cabinet of the PLC enclosure, such that the LED illuminates when the PLC's...
1,066
Hi, I have an ABB AC500 PM-582 PLC, The question is... is it possible to get the compiled code out of the CPU, i need to have this as a backup...
1,503
hi everyone i have this simple program using HSC i set the NEW_RV to 1000 when rotating the encoder and when reaching 1000 the counting restart...
1,582
My boss has come up with the idea of renting machines and charging on a per use / per hour basis, so I'm looking into it - just getting my feet...
4,000
Hi In one of our machine, there is Seimens PLC IM151-8 PN/Dp CPU. HMI is connected via Ethernet and other devices are connected via Profibus...
3,148