PLC 5 PID Instruction Question - Integral
Apr 2002
Burlington, Ontario
186
Hi all,
Got a quick question. Might be stupid and stright forward, but have to ask it. I have a loop being excecuted in a PLC5 PID loop, that needs to be tuned ( I don't usually do too much with PLC's) . My question is in regards to the integral gain value. We are using the "independent" form of the PID equation. According to the manual, the units on the integral are "1/seconds". So if my thinking is correct, the larger number entered for the integral gain, the "slower" the integral action will be??
Andrew Evenson
sorry ... you got it backwards ... with the "Independent Gains" equation, a BIGGER number gives MORE (faster) Integral action ...
PS Edit ... I just found this post that might be helpful ...
Hi Ron,
Thanks for your reply. After re-thinking about it you are right.
Does this make sense??
Gain value entered = 50
Therefore gain = 50 * (1/60) = 0.83333 - Larger gain, faster integral respose
Gain value entered = 0.1
Therefore gain = 0.1 * (1/60) = 0.00166 - Lower gain, slower integer reponse.
Again, thank-you very much for your reply.
Andrew Evenson
Hello, there is anyone who have already used hpmont plc? now i am programming for that plc and have " pid autotuning is not working" issue. I have...
980
Hai All, Am using GOC35 mitsubishi PLC in that plc i need a pid instruction in ladder format.so i used and i give a process value,set value...
1,739
82
Dear Fellows; Good day. Here i share two images one is PLC Sweep Time control and Monitor Screen and the other one PID Control Screen. First i...
242
Hi - I have an application where there is an option to use a PID loop embedded in the Transmitter to directly control (via 4-20mA output from the...
1,069