PLC CPU Error-Q02(H) Mitsubishi
zai_jnr
May 2008
MALAYSIA
169
Hi All,
I'm now working with PLC CPU Mitsubishi..CPU spec is Q02(H) CPU..
In this system there have networking Net-H (QJ71LP21-25) and master CC-Link (QJ61BT11)...
Now, there have error with CPU PLC...when diagnosis ..error code is 1403...What I've done now trying to replace new CPU,new NetH module, new CC-Link and new base unit..
but the problem was same...diagnosis after that was SP unit down...what need I do? all parameter setting is same as before replace new unit CPU...Help me please...o_O
Hi All,
I'am not really sure what to do, but did a search in the help file i GX IEC develpoer n 1403 error code:
Error code(SD0) 1403
Error message SP. UNIT DOWN
Common information(SD5-15) Module No. (Slot No.)
Individual information(SD16-26) -
LED status(RUN) Off/On
LED status(ERROR) Flicker/On
PLC operating state Stop/Continue
* In the QCPU except for remote I/ O module, either error stop or continue can be selected for each intelligent function module by the parameters.
Diagnostics timing When an END instruction executed /Always
Error description & cause
(1) The unsupported module is mounted.
(2) There was no response from the intelligent function module/special function module when the END instruction is executed.
(3) An error is detected at the intelligent function module/special function module.
(4) The I/O module (intelligent function module/special function module) is nearly removed, completely removed, or mounted during running.
Corrective action
(1) The CPU module, base module and/or the intelligent function module/special function module that was accessed is experiencing a hardware fault.
(2) When the unsupported module is mounted, remove it.
When the corresponding module is supported, this suggests the intelligent function module/special function module, CPU module and/or base unit is expecting a hardware fault.
(Contact your local Mitsubishi representative.)
Corrective action
Dear O_P,
Thanks a lot for your reply.. The problem solved...The root cause is from GOT bus cable..when, dismantle GOT cable from CPU..CPU can running as normal..but, when plug in the cable...CPU will error..
Dear Forum Members, We are having a TOSHIBA PLC EX40H which might be an obsolete Product. It is used on emergency diesel generator for its...
4,215
Fixes error indication "system configuration mismatch" the module of PLC VERSAMAX CPU I'm having the case of PLC VERSAMAX GEFANUC error. It is...
8,146
Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
91
Hi , Where i can find Mitsubishi PLC Card end of line & replacement model details. i am looking for Q02CPU replacement model. Please advice. thanks
132
Hey when I turn on my Siemens PLC CPU 216-2 after runing 10 minute it's stop and showing SF indication after I turn off and some time later turn...
127
