PLC General error fault
porky
Oct 2002
Maia
76
Hi all,
We have two Production Lines one controlled with a PLC 3 and the other with a PLC 5 AB. When starting up the second line,(two main compressors powered by 6000 volts with 2600KW and 2350 KW respectively) the first line shuts down with a PLC general fault. Take into account that this does not always happen, and that we can operate for months without problems. any sugestions ?? We are investigating our earthing.. (mixed power and instruments earths).
Any Ideas out there ??
I would need to know a great deal more about the wiring and the proximity of the PLC to the compressor starters & power lines etc...
DC relays making & breaking are murder on A-B PLCs, (induction & radio freq. from contact arc.)
Inductive kick from a large relay coil can cause problems.
Communication cables in close proximity to heavy currents.
You need to just start ruling out items, without knowing your system layout the first thing I would try is to power the PLC from a seperate clean source or UPS. Secondly, I would put suppressors across the coils of the compressor starters. Experiment, try to duplicate the problem when the facility is down.
With the problems so far apart it may take you a long time, I hate those kind of problems.
Good luck
Dear forum, I have earlier worked with RSLogix 5000 and I remember there was a function in the software that made it possible to save the current...
2,151
All, General Motors Corporation utilizes an PLC assessment for individuals applying for Journeyman Electrician positions. They utilize a 3rd...
2,842
Hi I have S7-1200 and want to use a general PC as HMI with TIA v.13 1) what additional hardware my PC should have? (it already has a TCP/IP...
3,931
Hi guys, Doing a conversion from PLC5 to Controllogix, and so far it's going smoothly. The programs are fairly simple, the errors are minimal...
2,212
Hey everyone I am very new to the use of PLCs and was performing a simple solar experiment for one of my courses and am kind of lost. My...
18
3,761