PLC Program & Routines
Ones_Zeros
Feb 2014
at work
367
Hello
I have a PLC test program that has a rung of logix in the "MainRoutine"
Its a simple rung that closes relay and makes the bit true and starts a timer.
I have 3 seperate programs labeled
Run1
Run2
Run3
In each of these seperate programs (Run1,Run2,Run3) I have a Memory bit tag with the same label called "Prestart"
I would like to close the relay located in the "Mainroutine" if any of the "Prestart" bits are true in programs (Run1,Run2,Run3)
Since these tags are labeled the same, how would I program these 3 tags
called "prestart" to close this relay and start the timer?
thanks
What version are you using? You could use parameters if v24+ otherwise controller scoped tags:
Define a controller scoped tag array such as Prestart[0..3]
In each of your "Run" programs create program scoped tag "Prestart" ALIASED to Prestart[1]C for Run 1 program, "Prestart" ALIASED to Prestart[2]C for Run 2, "Prestart" ALIASED to Prestart[3]C. This allows you to create identical code for each program, but the aliasing ensures unique controller scoped memory is used, thus giving you global access.
Your "MainRoutine" would then reference the controller scoped tags "Prestart[1]", "Prestart[2]" and "Prestart[3]" for evaluation outside the run programs.
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
90
Posted this to Reddit with little success, so I figured I would share it here as well. Very new to PLCs, but figured I would give it a shot to...
125
I'm a beginner in the automation field and I've set up an automation system connecting several devices (datalogger, radio, etc.) via Modbus RS485...
218
Hi All, want to ask. I have PLC a programme to control the valve. The existing programme is to control valve A (Y22), and I want to change to...
146
can anyone has a good program to learn plc programming online. i have the basic looking into improve my skills thanks
146