PLC selection advice needed for a simple system
NOContact
Feb 2010
Baltimore
The application is a control system for four fuel dispensers.
There are eight inputs:
Four contact closures (or 122V AC)
Four 122V AC sources
Six outputs:
Contact closures (or 120V AC)
The site is now controlled by:
Four time delay relays
Eight SPST relays
The logic is:
Fuel control system closes contact for a dispenser (contact closure or 122 VAC input to PLC)
Timer starts
And Start Pump & pipe leak detector (same contact closure or 120 VAC output from PLC)
When time for leak detection ends (timer), and dispenser's meter starts (122VAC input to PLC), then dispenser-valve opens (120 VAC output from PLC)
There are two fuel pumps, & four dispensers, two dispensers for each fuel.
The goal is to provide more reliable service, fewer points of contact failure, easier service, and lower cost. The cost is now $155 for relay parts and 8 hours for installation.
Are some models or brands better?
Thanks in advance for your advice.
It generally comes down to using what you know/what is available and supported in your area, and how much you want to spend. For something that seems relatively simple, you might try looking at Automation Direct or some other PLC that provides free/lost cost programming software.
You might want to look at something like an Allen Bradley pico. Basically a programable relay. The software is free. They can also be programmed through the small hmi on them. Not the most fun to do, but usable on a budget.
Thank you for your comments.
What do you think of the Click series?
"CLICK PLC CPU, 8 AC in / 6 relay out, requires a 24 VDC power supply; 8K steps program memory, 6.4K words data memory, Relay Ladder Logic programming; built-in RS232C programming port and additional RS232C Modbus/ASCII communications port (configurable up to 115.2K baud). Discrete Inputs: 8 AC inputs, 100-120 VAC, 2 isolated commons. Discrete Outputs: 6 relay outputs, 6-240 VAC / 6-27 VDC Form A (SPST) relays, 1.0A/point, 2 isolated commons. Removable I/O terminal block."
It looks like it fulfills your requirements that were listed in your first post. Because the I/O of the CPU is exactly what you need with no spares, the weak link is going to be the relay outputs. This is a common problem for all most all PLC brands.If you have a relay output go bad, you will not have to buy another CPU unit just buy an output module. If you leave room for the output module in your cabinet this will be easy. Relay outputs generally fail at at around 100,000 cycles. Pay attention to the surge suppression guidelines listed in the manual to get the best life from the relay contacts.
I did not see any current requirements in your original post, so I do not know if the relay outputs will be robust enough for your application. Another thing you did not mention is if your "relay closure" requirements need to be isolated from each other. In the CLICK model you are looking at I believe the first four relays have one "common" terminal and the next two relays have another "common" terminal.
The software is free and intuitive.
What are the implications of plc failure causing fuel to be pumped all the time ?
The result would be loss of usage tracking for filling school buses and owner's trucks. No financial impact as such. Oh, a phone call to me and rush to the site too.
Why do you ask? Is this a common mode of failure?
The same thing could happen with a welded contact though.
The system has a hand valve on the hose so there will not be fuel loss.
The PLC contacts are driving relays and solenoid valves. I have not checked the currents but should be able to find them in the manufacturer's data.
One should design with the idea of how to make this thing work as we want.
One should put double the time into design criteria
"what do we do if it screws up"
(power loss failed sensor etc etc). Couple best examples aircraft, train control, submarines, fuses, overload protection, emergency gravity brakes on elevators etc etc etc.
Dan Bentler
So, add code to detect and respond to unusual activity or lack thereof?
Timers on usage so that if left unattended, the delivery cannot be longer than it would take to fill an empty tank?
Also, it would be possible to easily reduce the wait time between filling the first and second tank by keeping the pump on and starting the dispenser without the normal time delay required by starting the pump. Naturally would have to include a time limit if no fueling is happening. . .
Trouble with the link
The link "http://www.gasboy.com/page/fleet_com...as_pump_gasboy " takes IE to a generic home page. Which device did you have in mind? The system now has a competitive controller (different manufacturer's), but it just controls a dispenser with one contact closure.
The installation needs to have a contact closure or 120VAC source on for five seconds before the dispenser can alow fuel to flow. This powers on a pump and permits a leak check on the piping before fuel can be dispensed. If the dispenser comes on at the same time as the pump, and someone opens the nozzle, the leak detector will restrict the flow from the pump. This results in very angry folks who have to wait a L O O O O O N N N N N G G time to fill the tanks. (There are also other controls that must operate in a particular order. The fueling system just does not provide the sequencing or contacts necessary.)
Need some help with AD: My friend who owns small shop wants to retrofit one of his machines with AD PLC. He took some time already trying to...
32
11,804
i have in my possesion some data sheets, i need to select a system that shall have 30 inputs to work wth 24V sensors and 30 outputs operating at...
3,436
Dear Members; We are going to design a Simplex Control System With Following: 1. 24 Digital Inputs (SIL 2) 2. 24 Digital Outputs (SIL 2) 3. 4...
1,132
Hello, Not able to find Modicon DO modules BMXDDO3202 in EcoStructure Control expert V15 catalogue. But i can find only MBXDDO3202K. Can you...
468
Good morning all, We want to build a test panel with IO link to get familiar with the product line. We have ML100's and SLC 5/03's currently...
1,628