PLC Upgrade from 1769 to 5069... Card Mapping Error
abarajas
Jun 2021
ks
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the Controller and i got "Error: Rung 0, CPS, Operand 0: Invalid member specifier.". Not sure on how to proceed with getting the new PLC to work.
5069_Mapping.png 5069
1769_Mapping.png 1769
Any help would be appreciated
It looks like the newer model doesn't have an equivalent "Data" tag. It looks like you would need to map each bit to the proper bit at your destination. Something like this, but going up to bit 15
OG
The issue is as OG describes; where in the 1769 module you had a single INT tag 'Data' containing the inputs from all channels, in the equivalent 5069 module each input is its own channel each with a separate BOOL for data.
I'm not aware of a way to map all the inputs in a single instruction the way you could previously, short of making your own AOI .
Hello all, I have a one problem. I would like to upgrade Mitsubishi PLC Q02 to Q03UDVCPU. I have Q02 program and I change to PLC type and try to...
192
I'm involved in upgrading an IDEC FC5A-D12S1E PLC to a FC6A-D32P3CEE. I've attached the original layout of the system. Since then, another HG3G...
458
Hello, I've recently tried to upgrade my PLC controller from a L72 to L84ES and everything seemed to work, all buttons and screens as far...
2,678
Hi, we are using 1756-L61 PLC redundant system in one location . due to some minor faults , we upgrade the firmware from 19.52 to 20.58. after...
1,353
I have a PLC that is version 13, and I want to upgrade it. Controller firmware is 13.25, using 13.04 software. It is a 1756-L55 What criteria...
3,000