PLC with no mains supply

Goody

Member
Join Date
Apr 2002
Location
Huddersfield W Yorks UK
Posts
1,081
Today I was called to a customer with an electrical fault on a machine. I have specialized a little on this type of machine and I have also written a program to retro-fit these machines, so I was glad to go. (I smelled a plc sale)

When I opened the control cabinet, There was already a plc doing the biz in there. (ah well, never mind, just repair the fault) The PLC was an old Mitsubishi F1.

As I was tracing the wiring (not a drawing or nowt you know) I looked at this plc and there was no mains voltage to it.
There were inputs and outputs wired and the outputs had a common 240V supply.
The mains voltage terminals had options for 240V and 110V but there was no wires in those terminals at all.
The plc had no lights on as the problem was with the main power contactor not coming on.

I found the fault (mangled wire) and put the power on.
The plc sprang to life with inputs and outputs going on and off but still with no supply to the L1 N1 N2 terminals. :confused:

I then found that there was another 24VDC supply and this fed the plc's 24VDC service supply. (the one you use for inputs)

This must be able to supply the plc with what it needed through the back door, because it works fine and the age of the plc means it must have been working fine for years. Has anyone seen this before?

I scratched my head for a good while. I was sure either the plc was not used or someone had been messing..............
 
You may want to check the specs on that Goody, alot of the older models had the option of using ac or dc, when ac was used the dc side could be used as a power supply but you could use a dc power source to power them with no ac applied. I dont know mitsi but many other brands did this.
 

Similar Topics

Hi all smart and knowledgeable people.I have a hmi connected to 2 Plcs via ethernet.These 2 Plcs connected to control 2 systems in one machine...
Replies
2
Views
81
Hello, We are now working on a software to collet the configuration of different PLC brands ,using a third software to backup all the simens...
Replies
1
Views
64
Dear Experts, I've come across an unusual piece of hardware for AB PLC-5 racks. I mean the NT-1776-HSD-R resolver input module. I have tried...
Replies
0
Views
39
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
12
Views
205
Hello all. I recently had to re install my AutoCAD Electrical 2024. I am trying to find the Rockwell catalog to install in it but cant find...
Replies
0
Views
98
Back
Top Bottom