Just wondering why I cannot set my Flex I/O ASB to rack 25.
I know 26 is reserved - checked the ASB using a different rack # - just not 25. No, 25 is not being used for anything else. And yes the processor has been mapped - to accept rack 25, group 0, starting 0, full rack.
Just trying to figure why rack 25 is a problem -- any similar issues and solution would be appreciated.
J Smith
From the RSLogix 5 Help file:
Valid addresses are 1-3 (octal) for PLC-5/20 processors,
3 (octal) for PLC-5/11 processors,
1-7 (octal) for PLC-5/30 processors,
1-17 (octal) for PLC-5/40 processors,
and 1-27 (octal) for PLC-5/60 and /80 processors.
That helped my rusty memory; I used mostly PLC-5/40's back in the day.
So, if you are using a 5/60 or 5/80 controller, you *should* be able to use rack 25 (octal).
How exactly does this failure manifest itself; does the Autoconfig fail to recognize the ASB, or does it just rack fault when you have it connected ?
Yep we have a 5/80 and the Autoconfig fails to recognize the ASB, and the rack faults when you manually set it up and connect.
If I assign the ASB to any other rack number, set the dip switches and set manual or autoconfig I have no problems - I therefore see no blue hose connection problem as it will "talk" at another adress.
Ok, I have to admit I have never setup a Flex to use such a high rack #. I quickly glanced the manual and did not see any reference to rack #26 being reserved by the system.
Can you setup any other device to Rack #25? Do they work? Lets see if it is a Rack 25 error or an ASB error!
What I would try next is to set it up as one rack higher and then one rack lower to see if those work (if those racks are available).
I know there was a mistake regarding the switch settings in previous manuals, have you double-checked the switch settings with the latest manual?
OG
Hi all, Quick question about maximum RIO for a PLC5. I'm looking to add some a RIO drop that emulates 6 racks to my existing PLC5 system (It is...
1,978
I am working for a company that does chrome plating and the line is VERY old lol So they did a controls upgrade(before my time here) and replaced...
1,792
I've been searching the forums for hours and I've found many things to try but just haven't found the right answer yet. I have a running PLC 5...
1,860
Can i terminate(put resistor in terminal of channel a)the blue hose of an existing plc5 dh+ network to a new 1756-dhrio in new clx rack without...
2,738
Hi everyone! I'm doing a upgrade here at the company. I`m replacing the Panelview 1400e to an 1500 plus. I`ve already made the tests on my pc by...
4,091