please help me ET 200
yuyo
Jul 2007
México
63
Hi guys.
I have a PLC 319F- 3PN, i do need configured so profinet ET 200 S, but i have many problems:
- i cant confugured hardware, becouse arent bad, many errors. the network profinet knowledge
can you help me.
Thank you.
Lot of more info is needed.
Is this totally new installation or old one which don't work anymore?
Is there any hardware differences between project and real cards?
(Attachments don't show configuration of ET200S, it is also hard to say from images what ET200S hardware you even have)
Can you ping ET200s IP address?
If this is new ET200S, Have you configured IP address for ET200S. From box every ET200 have IP address 0.0.0.0 and you need to configure it. (On your case ET200S should have IP 192.168.0.2)
thank you for answer
Its new installation
the card equal hardware
i have changed ip 192.168.0.3
some idea solutions
Do you have OB82, OB86 and OB122 in your program?
Just have the blocks in the program, and the CPU will not go to stop.
Look in the diagnostic for the CPU to see what the problem is (ctrl + D)
Check every part number of the modules in the ET200S rack compared to your Hardware Config. They must match 100%. Check that the termination module of the rack is installed on the very right of the ET200S rack.
By the way, it looks like your first module is not inserted properly.
can you please on line remote team viewer
Hi ! Everybody ! Please..help me about communication between S7 1200 and inverter or any varispeed inverter had MODBUS support by module CM1241...
20
11,183
Hi guys! I'm Leandro from Argentina, and i'm starting to write on this great forum for the first time. I always read your treads, and I have to...
3,674
Good day all. I am troubleshooting a Micrologix1200 (1762-L40BWA) with a Bul.1762, ser C processor. I have two questions, please. I have the...
3,041
Hey good peoples, I’m a sparky and do the low level PLC work whenever I get the chance though it has been many years since I’ve done any PLC...
8,235
Hello everyone. Thanks for taking the time to read my question. I would consider myself a advanced-beginner PLC programmer. I've used the Siemens...
4,604