PointIO chassi size conundrum
spaderkung
Aug 2007
South Sweden
389
I'm probably a spoon now, but designing the PointIO node offline with som DI, DO, EP24DC, FPD I get a chassi size of 12. Not possible to set lower in the menu.
Online I get the Christmas tree of death on the node. It reports a chassi size 11. I set it online and all is green.
There is a total of 11 IO cards. 12 including the AENTR.
Please help me understand.
BR
Jon
No, that would make too much sense.
You must use Linx to actually set the rack size.
Auto-discovery might work, but I never bother with it since it is a "Rockwell Feature", and not to be trusted.
This may be plc platform dependent. I was not a user of either Point I/O or the Logix platform in the early days of either platform and I have only used Point I/O with Logix platform controllers. But in all cases I have used Point I could set the chassis size in the adapter from the I/O properties pop-up in the Logix5k development environment without having to use RSLinx.
Having said that it is kind of silly that the plc doesn't automatically set this value on start-up.
Keith
This thread is referring to setting the chassis details in the 1734-AENT when you go online. Unless I miss my guess the screen shot you show is for setting the chassis size in development so you can add modules to your Point group.
Keith
I'm working with a 1734-AENT PointIO module (manual) connected to a 1769-L30ER controller over fiber ethernet. The 1734 PointIO module has some...
1,056
Hello all, I Have a PointIO module with 2 input cards. The Revision is 6.013 and it is connected to a ControlLogix running version 24.11 The...
2,387
A customer has a stamping press that has 2 DeviceNet nodes going to a DeviceNet control card in a ControlLogix rack. Older ControlLogix, L55...
41
15,127
Hi, I'm having issues commissioning a new PointI/O module (1734-4IOL) on an existing DeviceNet network (1756-DNB). I am adding the 4IOL module to...
837
Is it possible or advisable to remove an RTB, then reinsert a new RTB on a 1734-AENTR without power cycling? This is done with modules of course...
1,899