We have approx 100 PF40 conveyors in our building. Occasionally one stops without a fault being sent to the PLC. We reset/start the conveyor and it runs OK.
When I check the PF40 Fault Queue I always see: F4 F71 F4, indicating DC Buss Undervoltage, followed by the Comm Loss. We are using Profibus, and when I run Profitrace, the buss checks out normal.
I'm wondering if the motor startup load can momentarily bring the AC Buss down along with the DC Buss, enough to cause the Comm Card to glitch, resulting in the F71 Fault?
TIA for your feedback...
You can get an F4 DC bus undervoltage when you have a lost or intermittent incoming phase, because the DC bus ripple becomes excessive for the load on the drive. It can also be an early indicator that the DC bus caps are starting to fail. But yeah, the comm card is powered from a DC/DC power supply that is tapped off of the main DC bus, so if the main DC bus goes wonky, the PSU for thee comma card may wink out.
Thanks, That's helpful!
Is there a diagnostic I can run to check the health of the DC Buss Caps?
Most of the Drives in my building are 5 years old, and they run 20 hours per day, 7 days per week, so many are > 30,000 hours.
is it possible to comunicate a powerflex 753 (ccw) using ethernet 20-750-ENETR card to a panelview plus 6 1250 (factorytalk view studio me)...
1,498
I usually access online view of Powerflex by opening the drive module property menu and open the "drive" tab. However, I cannot access the...
1,474
Hi! I have a powerflex 4M frequency driver and a S7 1200 in a control cabinet. My customer wants some times in the PLC to be changed based on the...
1,560
Hi! I'm using the 1763-nc01 and AK-U0-RJ45-TB2P to connect these devices. I've tried to find manuals for these but wherent so succesfull. I dont...
1,567
All power flex inverters are suffering from F71 fault randomly across the Device net network which cause Operation to stop. As a resolution from...
3,226