Hi folks,
We are looking at installing sometype of instrument to monitor our power, I'm currently investigating the GE PQM II. I'm open to suggestions for other brands also.
Has anyone used this before?
Does GE have a software package that would allow us to use a cheap PC for data collection vs. connecting to the current control system? The PQMII "speaks" MODBUS, and at this location, there are no existing MODBUS networks.
Assuming the software is $1000.00 or less, it would be cheaper to buy the software and a PC.
Thanks in Advance,
Ken
Square D used to have some very nice monitoring tools, but I am not sure what they have know. The last time I was involved in power systems was almost 10 years ago.
We have a rather extensive power/energy monitoring system. We use mostly AB PowerMonitor 3000's. They are available in a variety of communication configurations. Modbus,Ethernet IP, ControlNet, RIO etc. They are available in a couple of different levels of accuracy/functionality. It depends on what you need. They can even do Harmonics I think. They can also collect Min/Max data. We don't use nearly all of their functionality.
Ours are all Ethernet IP. They have an on board Web Server. You can look at the current power conditions via Internet explorer. You could also use RSlinx and Excel to poll and log data if you wanted.
We use RSEnergy Metrix to data log all of our information. It is pretty expensive if I recall. Like I said we monitor a lot of systems though. We monitor Water, Steam, Compressed air, Central Vacuum, Ammonia Refrigeration, Comfort Cooling, Local Weather Data, and Electrical Power.
RSL
The GE software is here Kenhttp://www.geindustrial.com/cwc/products?famid=14&catid=55&lang=en_US
I have used the AB power monitor 3000 devices on Device Net into Omron PLCs and than on to Citect SCADA. Theya are very good and do monitor harmonics.
For something a little less expensive if %THD will do, try the Crompton Instruments 1534 series. Modbus, Johnson Controls etc available. Class 0.2 (0.2%) accuracy - very good actually. Use these things all the time - they are less than half the price of the AB ones and I have never had one fail. Here is a link to the manual
http://www.crompton-instruments.com/integra/us_din_1530.pdf
Square D had a group that wanted to develop PLC compatible power monitoring. They worked out of the Cedar Rapids circuit breaker plant - before...
834
Trying to find/understand how best to monitor the current in a three phase circuit with a PLC. Need an analog signal that can be monitored by an...
5,773
I have an AB SLC 5/05 and i want to modify the program to so that i can monitor and record the power being used by the electric motor when its...
1,578
Hi all, I need to communicate with 28 Circutor PMU(Power monitoring unit )using a control logix 1756-L61. Problem is that these PMU uses MODBUS...
4,189
Hi Guys, i have a micrologix 1100 and want to use its analogue input to measure a 12v battery voltage level using resistors. I want to know whats...
7,240