Hi everyone !
A multiconductor wire 4x2,5mm2 would be ok ?
Normally a 10hp - 400V motor would pull 16-17A
A 4x2,5mm2 wire could carry around 21-22A according to many manufacturers,
Considering the wire will be on open strays, at open space and next to other small conductors, length of 30m max.
I know a wire of 4x4mm2 would be better,
But would 4x2,5 be a problem ?
The cable is copper and PVC
Thanks!
A multiconductor wire 4x2,5mm2 would be ok ?
Normally a 10hp - 400V motor would pull 16-17A
A 4x2,5mm2 wire could carry around 21-22A according to many manufacturers,
Considering the wire will be on open strays, at open space and next to other small conductors, length of 30m max.
I know a wire of 4x4mm2 would be better,
But would 4x2,5 be a problem ?
The cable is copper and PVC
Thanks!