Powerflex 40. Output Current vs Torque Current
Tharon
Jan 2007
Other
1,430
I was looking at the Display Group parameters on a couple of our Powerflex 40s that were having OL faults today. And I noticed there were two display options for Current:
d003 - Output Current
d029 - Torque Current
Could someone help me understand the difference between those two? I didn't see anything in the Manual (22B-UM001H) but I suspect that they are defined terminology that I should probably already know.
Thanks.
Some of the current going to the motor is just turning the copper and steel from being a bad excuse for a boat anchor into a spinning motor, then some of the current is actually producing torque. The Output Current reading is ALL of the current going to the motor inclusive of the torque producing current, the Torque Current is telling you how much of the current is actually producing torque. Essentially if the motor is unloaded, more of the current flowing into it is reactive current due to the poor motor Power Factor, vs when fully loaded almost ALL of the current will be torque producing current. This is something that only really matters when you are in Vector mode, because in V/Hz mode the VFD is not really tracking the difference, it just looks at the total current. If you compared d022 and d023, Output Power and Outpur Power Factor, you would see the relationships to all of those values.
Funny, this same issue came up in another thread just today on 755 drives...
Ok, makes a bit more sense. This motor is running just in V/Hz mode. And the load was definitely up there, the Torque Current was reading 7.0A on the drive, and the FLA of the motor is 3.3A, with drive Overload Current set to 3.4A
I think I may need a larger motor for the application (Sawing).
Hi everyone, I have a AB Powerflex 753 powering a simple 480V permanent magnet motor using flux vector control (I believe it's the only control...
1,358
Good Morning , I am working on a project with some PowerFlex 525 drives. I am using CompactLogix 1769-L18. I took notice that the tags that...
23
22,568
Just wondering if anyone has run into a powerflex 753 has all the incoming power, but doesnt output any power to the motor, but doesnt display any...
1,641
Hey Guys, I am wondering if it is possible to wire an output from PLC to the start enable terminal (2) on the powerflex 40. as far as i can see...
1,700
Hi guys, I'm working on a new project and we have Allen Bradley Powerflex 753 VFDs controlling oxidation ditch aerators. I'm not currently...
3,188