Powerflex 70 / HW OverCurrent Fault #12 - What is the common reason for this fault ?
Cydog
Feb 2018
Maryland
314
Good Afternoon ,
I have a Powerflex 70 Drive . It faulted out with a #12 HW OverCurrent Fault .
With your experience , what is the common cause of this fault ?
Thanks so much .
That means the output current of the drive exceeded the limit. If it's been running fine for a while and then started faulting, I would first check the load. If possible, de-couple the motor and see if the motor bearings ok and if there's any mechanical wear or binding in the driven load.
Have had this same fault caused by loose/bad wiring, bad motor & bad remote disconnect. As I recall, HW Overcurrent means the drive is seeing 2.5x the motor nameplate current.
The F12 Hardware Overcurrent is an "instantaneous overcurrent" protection feature built into the transistor section of the drive, rather than analyzed by the firmware running on the main control board.
Typically it means the drive is observing 220 to 300 % of the output current rating of the drive itself; the percentage depends on the frame style.
The most common reason for that fault is a wiring or motor failure that is turning a lot of current into heat.
But there are other reasons, which can include motor selection and basic drive configuration. Which is the most likely can, of course, depend on where you are in the drive's application lifecycle.
The RA Knowledgebase has a good general troubleshooting guide for F12 HW Overcurrent (Access Level: Everyone).
https://rockwellautomation.custhelp.com/app/answers/answer_view/a_id/107475/loc/en_US
F12 fault
To be more clear, the most common cause of this fault is a shorted wire (L1 L2 L3/UVW inside the pecker head. What I do is set auto retries (A092) to 9 and watch for the phase loss fault to show, (F41/F42/F43). I’ll bet it’ll be right there when you open the pecker head. Sometimes you’ll have to look beneath where the wires go inside the shell of the motor, but it’s there.
Running a Powerflex 700 VC 40, two 10 hp motors in parallel with their own overcurrent protection, FVC mode, Intertia autotune done, external...
7,100
Hi everyone, I have a AB Powerflex 753 powering a simple 480V permanent magnet motor using flux vector control (I believe it's the only control...
1,367
Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
137
Hello Everyone, I want to upgrade the firmware of Powerflex 40 from 5.001 to 6.002 can anyone tell me how can I do that?
75
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
255